Posted: Fri Feb 22, 2008 3:50 pm Post subject: 220 VOLT COMPRESSOR |
|
|
Bob,
I had a 120 volt air compressor and change to a 220 volt model thinking I would save some on my electrical bill.
I was under the impression that the amp’s being drawn would be cut in half when going to 220V.
A friend says the 220 v motor will still draw the same amps. That each leg of the 220 v will draw half the amp’s but the combined draw is still the full draw of the 110 v.
I told him that hat is correct but that one leg of the 220 v line will be out of phase with the other, so only half the amps are being required.
Is this correct?
Thanks
John L. Danielson
[quote][b]
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
bob(at)bob-white.com Guest
|
Posted: Fri Feb 22, 2008 4:19 pm Post subject: 220 VOLT COMPRESSOR |
|
|
On Fri, 22 Feb 2008 16:47:24 -0700
"John Danielson" <johnd(at)wlcwyo.com> wrote:
Quote: | Bob,
I had a 120 volt air compressor and change to a 220 volt model thinking I
would save some on my electrical bill.
I was under the impression that the amp's being drawn would be cut in half
when going to 220V.
A friend says the 220 v motor will still draw the same amps. That each leg
of the 220 v will draw half the amp's but the combined draw is still the
full draw of the 110 v.
I told him that hat is correct but that one leg of the 220 v line will be
out of phase with the other, so only half the amps are being required.
Is this correct?
Thanks
John L. Danielson
In a word, no, it is not correct. You are going to need a certain
|
amount of power depending on the HP rating of your electric motor.
Maybe the 220V motor is a little more efficient, but I don't think
much. You do get some benefit from lower losses in the 220V circuit
because of the lower current. If you need a really big compressor (big
motor) you might need to go to 220V because you can't deliver enough
current at 120V. For the record, both 120 and 220 circuits are single
phase. The current in the common between the two phases is zero, but
all the current you are using is flowing in the hot wires.
All said, there are advantages to going to 220V, but you won't be
saving 1/2 the power when running the same size compressor.
Bob W.
--
N93BD - Rotary Powered BD-4 - http://www.bob-white.com
3.8 Hours Total Time and holding
Cables for your rotary installation - http://roblinstores.com/cables/
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
JOE RONCO
Joined: 04 Aug 2007 Posts: 31 Location: CENTENNIAL COLORADO
|
Posted: Fri Feb 22, 2008 5:50 pm Post subject: 220 VOLT COMPRESSOR |
|
|
JOHN: >From my limited electrical knowledge, HP = Watts (746 watts = 1 HP). Watts = Volts x Amps. Your power bill is paid on the number of Watts used. For a given HP motor the Watts is the fixed, so at 220 Volts you will have the same Watts but half the Amps that you would have with 110 Volt power supply. Therefore your power bill will not change.
Hope this makes sense.
Joe Ronco.
From: owner-aeroelectric-list-server(at)matronics.com [mailto:owner-aeroelectric-list-server(at)matronics.com] On Behalf Of John Danielson
Sent: Friday, February 22, 2008 4:47 PM
To: aeroelectric-list(at)matronics.com
Subject: 220 VOLT COMPRESSOR
Bob,
I had a 120 volt air compressor and change to a 220 volt model thinking I would save some on my electrical bill.
I was under the impression that the amp’s being drawn would be cut in half when going to 220V.
A friend says the 220 v motor will still draw the same amps. That each leg of the 220 v will draw half the amp’s but the combined draw is still the full draw of the 110 v.
I told him that hat is correct but that one leg of the 220 v line will be out of phase with the other, so only half the amps are being required.
Is this correct?
Thanks
John L. Danielson
Quote: | http://www.matronics.com/Navigator?AeroElectric-List | 0123456789
[quote][b]
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
rv-9a-online(at)telus.net Guest
|
Posted: Fri Feb 22, 2008 10:14 pm Post subject: 220 VOLT COMPRESSOR |
|
|
Quote: | Bob,
I had a 120 volt air compressor and change to a 220 volt model
thinking I would save some on my electrical bill.
I was under the impression that the amp's being drawn would be cut in
half when going to 220V.
A friend says the 220 v motor will still draw the same amps. That each
leg of the 220 v will draw half the amp's but the combined draw is
still the full draw of the 110 v.
I told him that hat is correct but that one leg of the 220 v line will
be out of phase with the other, so only half the amps are being
required.
Is this correct?
|
Theoretically, if you are consuming the same volume of air at a given
pressure, a 110 and 220 compressor will consume the same energy and the
average powers will be the same. (other than slight differences between
compressor types and design).
Vern
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
rv9jim(at)juno.com Guest
|
Posted: Sat Feb 23, 2008 6:52 am Post subject: 220 VOLT COMPRESSOR |
|
|
John,
Your are paying for power. 1 kw is still 1 kw whether you do it
with lower voltage and higher current or higher voltage and lower
current. It all comes out the same. The real advantage with the 220v
system is you can use smaller wire in setting up the system. The losses
in the system are smaller with the higher voltage. Not enough to matter
in this case. I run my compressor off my dryer circuit which is a 30a
circuit. Since I went with gas for drying, that circuit was available
with just a plug and a bit of wire to a manual disconnect at the
compressor.. (you need that).
Jim
off to the painter
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
gmcjetpilot
Joined: 04 Nov 2006 Posts: 170
|
Posted: Sat Feb 23, 2008 7:37 am Post subject: 220 VOLT COMPRESSOR |
|
|
John:
You did the right thing but.... not to save money.
Unless you are running a factory with hundreds of
AC motors money saving on the electrical bill is
not the issue.
Some synchronous AC motors have a leading power
factor (look it up) and thus exploit how the utility
companies charge you. However a compressor
duty is pretty small and again we are talking about
once relatively small compressor.
Get a 220 Compressor, not to save electricity but to
have more power to make more air. The 220 volt motor
is more efficient for the job and you may save some
electricity, if comparing HP to HP, but the issue is
getting enough HP with 110 volts to drive a compressor
that is large enough to make enough volume of air fast
enough for the application. Air tools and Pro painting is
very air intensive applications. The surge current to start
a large compressor is huge and you need a 220 v motor
to get a bigger compressor going at all. If all you do is
fill some tires or beach balls, than 110 v is OK.
The small effort to wire in a 220 plug is small.
HOWEVER BE Careful, electricity can kill you. If in
doubt get a Pro and spend the money, or get help.
Yes house current is 220 Volt AC, 60 Hrz, with two hots
and one neutral.
-Any / either hot to neutral is 110 Volt.
-Hot to Hot is 220 volts.
-If you do any wiring than TURN off all electricity and BE
-very very careful.
-The ground is ground for 110 or 220 volt.
Just be careful. If anyone is going to rivet a RV together
or paint anything, get 220 V. Get a REAL compressor
not a Sears 110 v oil less toy compressor.
If you want to learn about AC motors single phase or
multi phase check the Google.
http://en.wikipedia.org/wiki/AC_motor
There is a thing called the "power factor" and it is how
the utility company chargers you. AC electrical power
engineering has terms like "real pwr", "apparent pwr"
and "reactive power". Google this for an explanation.
Again one little compressor for a hobby? No big deal.
George
PS if you do the wiring write me I can help you.
Quote: | From: "John Danielson" <johnd(at)wlcwyo.com (johnd(at)wlcwyo.com)>
Subject: 220 VOLT COMPRESSOR
|
Bob,
I had a 120 volt air compressor and change to a 220
volt model thinking I would save some on my
electrical bill.I was under the impression that the
amp's being drawn would be cut in half when
going to 220V.
A friend says the 220 v motor will still draw the
same amps. That each leg of the 220 v will draw
half the amp's but the combined draw is still
the full draw of the 110 v.
I told him that hat is correct but that one leg of the
220 v line will be out of phase with the other, so
only half the amps are being required. Is this
correct?
Thanks John L. Danielson
Be a better friend, newshound, and [quote][b]
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
|
|
|
You cannot post new topics in this forum You cannot reply to topics in this forum You cannot edit your posts in this forum You cannot delete your posts in this forum You cannot vote in polls in this forum You cannot attach files in this forum You can download files in this forum
|
Powered by phpBB © 2001, 2005 phpBB Group
|