Matronics Email Lists Forum Index Matronics Email Lists
Web Forum Interface to the Matronics Email Lists
 
 Get Email Distribution Too!Get Email Distribution Too!    FAQFAQ   SearchSearch   MemberlistMemberlist   UsergroupsUsergroups   RegisterRegister 
 ProfileProfile   Log in to check your private messagesLog in to check your private messages   Log inLog in 

Air compressor tripping circuit breaker
Goto page 1, 2  Next
 
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> RV10-List
View previous topic :: View next topic  
Author Message
Deems Davis



Joined: 09 Jan 2006
Posts: 925

PostPosted: Tue Sep 23, 2008 2:39 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

I'm moving the 'shop' from the garage to the hangar. I've been using a
25 yr old Campbell Hausfeld air compressor which has a motor which it
say's draws 15 amps (at) 115VAC . It would frequently trip the garage
circuit, which I 'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the compressor
trips the breaker every time it plugged in. The airport service
personnel are getting annoyed at me calling for them to come out and
reset the breaker.
DC electricity was/is a challenge to me, so this AC stuff is way
beyond my understanding. I looked at Lowes for a new compressor, but it
appears that most of the ones suitable to run the air tools all come w/
15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which will
not trip? What are you guys using at the hangar?
Deems

not so patiently waiting on my painter...............


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
View user's profile Send private message Send e-mail
pitts_pilot(at)bellsouth.
Guest





PostPosted: Tue Sep 23, 2008 3:02 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

The problem is the startup current of the motor. The start winding
draws a lot of current getting up to speed where the run winding takes
over .... and uses less current. Typically the oilless compressors work
better, but you won't get the volume you're used to. It's a trade off.
The other problem is how far from the breaker box you are. Hangar
wiring is notoriously small .... the hangars were designed to house
airplanes .... not be manufacturing facilities. When we built new
hangars at my airport I inquired if we could increase the current
capability by paying a little more for the increased cost of the
wiring. Hangars are designed with a power density .... so much power
per sq. foot. I wanted 220 available for my big compressor and paid an
extra $150 for the addition, and it was drawn into the plans. It was
cooperation with the airport that made the difference.

Now for a little 'cheat' ...... typically hangars are wired so that
every other hangar is on the same leg of the 220. If you steal the hot
leg from the hangar next to you, and use your leg, you have 220 service,
and the 15A breakers will do just fine ...... unless you're on the
opposite end of the hangar from the breakers!
Linn
Deems Davis wrote:
Quote:


I'm moving the 'shop' from the garage to the hangar. I've been using a
25 yr old Campbell Hausfeld air compressor which has a motor which it
say's draws 15 amps (at) 115VAC . It would frequently trip the garage
circuit, which I 'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the
compressor trips the breaker every time it plugged in. The airport
service personnel are getting annoyed at me calling for them to come
out and reset the breaker.
DC electricity was/is a challenge to me, so this AC stuff is way
beyond my understanding. I looked at Lowes for a new compressor, but
it appears that most of the ones suitable to run the air tools all
come w/ 15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which
will not trip? What are you guys using at the hangar?
Deems

not so patiently waiting on my painter...............


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
pascal(at)rv10builder.net
Guest





PostPosted: Tue Sep 23, 2008 3:07 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

I have a Craftsman 2HP 25 gallon
http://www.sears.com/shc/s/p_10153_12605_00919541000P same amps but never
has been an issue for me with a 15amp circuit and other electrical items
running on the same circuit.
You may want to assure that your CH is running alone with nothing else
running when you have it compress air. I turn my off "auto" and manually
select to have it load up again at my timing not whenever it feels it needs
it. The result is never a popped circuit.
Pascal

--------------------------------------------------
From: "Deems Davis" <deemsdavis(at)cox.net>
Sent: Tuesday, September 23, 2008 3:38 PM
To: <rv10-list(at)matronics.com>
Subject: Air compressor tripping circuit breaker

Quote:


I'm moving the 'shop' from the garage to the hangar. I've been using a 25
yr old Campbell Hausfeld air compressor which has a motor which it say's
draws 15 amps (at) 115VAC . It would frequently trip the garage circuit,
which I 'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the compressor
trips the breaker every time it plugged in. The airport service personnel
are getting annoyed at me calling for them to come out and reset the
breaker.
DC electricity was/is a challenge to me, so this AC stuff is way beyond
my understanding. I looked at Lowes for a new compressor, but it appears
that most of the ones suitable to run the air tools all come w/ 15 amp
motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which will
not trip? What are you guys using at the hangar?
Deems

not so patiently waiting on my painter...............




- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
ricksked(at)embarqmail.co
Guest





PostPosted: Tue Sep 23, 2008 3:21 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Have them replace the breaker with 20 amp, it should be 12-2 wire and plenty enough to handle the load plus the breaker may be shot anyhow
---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
Kelly McMullen



Joined: 16 Apr 2008
Posts: 1188
Location: Sun Lakes AZ

PostPosted: Tue Sep 23, 2008 3:22 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Hmm, Home Depot has Husky 30 gal that is what I am using..but I have
20 amp circuit at the hangar, but I also am running all the lights on
same circuit. Lowes has equivalent Kobalt. Both are oil lubed, belt
driven compressors that I think have much lower starting current than
the oil-free pumps.

On Tue, Sep 23, 2008 at 6:38 PM, Deems Davis <deemsdavis(at)cox.net> wrote:
Quote:


I'm moving the 'shop' from the garage to the hangar. I've been using a 25 yr
old Campbell Hausfeld air compressor which has a motor which it say's draws
15 amps (at) 115VAC . It would frequently trip the garage circuit, which I
'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the compressor
trips the breaker every time it plugged in. The airport service personnel
are getting annoyed at me calling for them to come out and reset the
breaker.
DC electricity was/is a challenge to me, so this AC stuff is way beyond my
understanding. I looked at Lowes for a new compressor, but it appears that
most of the ones suitable to run the air tools all come w/ 15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be 'fixed'
to not trip the breaker, can it be replaced with one which will not trip?
What are you guys using at the hangar?
Deems

not so patiently waiting on my painter...............


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List

_________________
Kelly McMullen
A&P/IA, EAA Tech Counselor
KCHD
Back to top
View user's profile Send private message
Kelly McMullen



Joined: 16 Apr 2008
Posts: 1188
Location: Sun Lakes AZ

PostPosted: Tue Sep 23, 2008 3:51 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Not at most city owned hangars. It isn't uncommon for more than one
hangar to share a breaker, and wiring often is 14-2. They are not
interested in increasing capacity for owners. However, Deems, at DVT
there are relatively new outlets on the shades in front of the hangars
and they may be higher capacity.

On Tue, Sep 23, 2008 at 7:17 PM, <ricksked(at)embarqmail.com> wrote:
[quote]

Have them replace the breaker with 20 amp, it should be 12-2 wire and plenty enough to handle the load plus the breaker may be shot anyhow
---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List

_________________
Kelly McMullen
A&P/IA, EAA Tech Counselor
KCHD
Back to top
View user's profile Send private message
jesse(at)saintaviation.co
Guest





PostPosted: Tue Sep 23, 2008 4:25 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

I guess it's time to break out the Y2K generator. Smile. Or, just break
in one night and slip on a 20A, but you have to be prepared to
categorically deny the charges (and have a good alibi) when your
hangar burns down or become a fugitive (I hear Ecuador is nice this
time of year).

Do not archive

Jesse Saint
Saint Aviation
jesse(at)saintaviation.com
352-427-0285

On Sep 23, 2008, at 6:38 PM, Deems Davis <deemsdavis(at)cox.net> wrote:

Quote:


I'm moving the 'shop' from the garage to the hangar. I've been using
a 25 yr old Campbell Hausfeld air compressor which has a motor which
it say's draws 15 amps (at) 115VAC . It would frequently trip the
garage circuit, which I 'patched' by putting in a larger (20A)
breaker.
Well, the electric service to the hangar is 15 amps, and the
compressor trips the breaker every time it plugged in. The airport
service personnel are getting annoyed at me calling for them to come
out and reset the breaker.
DC electricity was/is a challenge to me, so this AC stuff is way
beyond my understanding. I looked at Lowes for a new compressor,
but it appears that most of the ones suitable to run the air tools
all come w/ 15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which
will not trip? What are you guys using at the hangar?
Deems

not so patiently waiting on my painter...............



- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
partner14



Joined: 12 Jan 2008
Posts: 540
Location: Granbury Texas

PostPosted: Tue Sep 23, 2008 5:04 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Boy, this discussion really makes us sound like a bunch of sneeky old men.... oh, I guess we are! I have a compressor I bought at Home Depot, can't remember which one, but it has 3 speeds. So you could find which speed you can use without tripping the breaker. My hanger has a junction box in the center overhead. When I openned it up, I found that they had terminated all the wires with wire ties that lead to the rest of the hangers down the line. So naturally I tied into one of them, and now I have 2 20amp services.... one for each side of the hanger. Don

--- On Tue, 9/23/08, ricksked(at)embarqmail.com <ricksked(at)embarqmail.com> wrote:
[quote]From: ricksked(at)embarqmail.com <ricksked(at)embarqmail.com>
Subject: Re: Air compressor tripping circuit breaker
To: "Rv" <rv10-list(at)matronics.com>
Date: Tuesday, September 23, 2008, 4:17 PM

[quote]--> RV10-List message posted by: ricksked(at)embarqmail.com Have them replace the breaker with 20 amp, it should be 12-2 wire and plenty enough to handle the load plus the breaker may be shot anyhow ---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List

_________________
Don A. McDonald
40636
Back to top
View user's profile Send private message Send e-mail
Tim Olson



Joined: 25 Jan 2007
Posts: 2872

PostPosted: Tue Sep 23, 2008 5:04 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Well, you can't just change the breaker, as was suggested. You need
to KNOW that the wire is not only of the proper gauge, but not
over a certain length, also. If you have extremely long runs back
to the fuse panel, as some hangars are, you may need to have either
larger wires run, or larger wires AND an increased breaker size, IF
that still works for the overall panel rating and usages. So it's
not just something you can do a quick fix on....it takes someone
who knows the requirements to do it right. Any less and you're
risking yours and other peoples airplanes to fire. In my hangar,
I was routinely tripping my breaker, one circuit that runs the
doors, lights, and everything, when I ran the compressor.
I took care of it a few ways...

First, when I run the door, everything else is off. The startup
current on the door required that.

Later, when I needed the compressor, I was tired of resetting
the breaker all the time. One thing helped a little....letting
the compressor run out of air before you started it. Startups
where the piston has to get moving against high pressure took
more torque. So an empty tank is less likely to trip the
breaker....although that might not be enough.

Ultimately, the permanent solution for me was: I left the
door and lights on the existing circuit. I then pulled some
nice heavy wire....I think 8 or 10ga, and put in 2 new circuits.
A 4-gang outlet back by my workbench...so the compressor would
have a minimum of cord length (which helps....the voltage
drop on the line will cause a higher starting current if you have
long wire runs), and then I put a couple other outlets near
the sides of the plane that were on those new circuits. Now
all of my tools get plugged into the heavier capacity circuit.

So in the end, probably the best way to fix it is to hire an
electrician to pull another circuit into your hangar just for
your tools. In the long run it's a few hundred bucks well spent.

Tim Olson - RV-10 N104CD - Flying
do not archive
Deems Davis wrote:
Quote:


I'm moving the 'shop' from the garage to the hangar. I've been using a
25 yr old Campbell Hausfeld air compressor which has a motor which it
say's draws 15 amps (at) 115VAC . It would frequently trip the garage
circuit, which I 'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the compressor
trips the breaker every time it plugged in. The airport service
personnel are getting annoyed at me calling for them to come out and
reset the breaker.
DC electricity was/is a challenge to me, so this AC stuff is way
beyond my understanding. I looked at Lowes for a new compressor, but it
appears that most of the ones suitable to run the air tools all come w/
15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which will
not trip? What are you guys using at the hangar?


Deems

not so patiently waiting on my painter...............



- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
View user's profile Send private message Send e-mail
DLIUDVINAITIS(at)aol.com
Guest





PostPosted: Tue Sep 23, 2008 6:08 pm    Post subject: Air compressor tripping circuit breaker Reply with quote

Deams

Do not change the breaker to 20 amp. the wire in hanger is problem 14-2 wire rated gauge. a 20 amp circuit would have a 12-2 wire rated gauge, as stated by others this could cause a fire or trips from motor starts (higher amp pulls). Deams your 25 yr old compressor might be the problem. 1) I would drain & change the compressor oil to lower viscosity (buy (at) homedepot or sears). 2) check belt tension. to tight this will cause higher startup amps ( need amp meter to check) look (at) motor plate to find runnning amps. hope this can help if not recommend electrican or just buy newer compressor.

Dave Ludd
40466 NJ,

In a message dated 9/23/2008 5:40:47 P.M. Central Daylight Time, deemsdavis(at)cox.net writes:
Quote:
--> RV10-List message posted by: Deems Davis <deemsdavis(at)cox.net>

I'm moving the 'shop' from the garage to the hangar. I've been using a
25 yr old Campbell Hausfeld air compressor which has a motor which it
say's draws 15 amps (at) 115VAC . It would frequently trip the garage
circuit, which I 'patched' by putting in a larger (20A) breaker.
Well, the electric service to the hangar is 15 amps, and the compressor
trips the breaker every time it plugged in. The airport service
personnel are getting annoyed at me calling for them to come out and
reset the breaker.
DC electricity was/is a challenge to me, so this AC stuff is way
beyond my understanding. I looked at Lowes for a new compressor, but it
appears that most of the ones suitable to run the air tools all come w/
15 amp motors.

Anybody got any suggestions ? Can the motor on my old compressor be
'fixed' to not trip the breaker, can it be replaced with one which will
not trip? What are you guys using at the hangar?
Deems

not so patiently waiting on my = es y --> - MATRONICS WEB FORUMS nbsp; - List Contribution Web Site ;   =========================



Looking for simple solutions to your real-life financial challenge/aol?redir=http://www.walletpop.com/?NCID=emlcntuswall00000001" href="tp://www.walletpop.com/?NCID=emlcntuswall00000001" target="_blank">Check out WalletPop for the latest news and information, tips and calculators.
[quote][b]


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
rv(at)thelefflers.com
Guest





PostPosted: Wed Sep 24, 2008 2:18 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Before I was in the aircraft building business, I purchased a small pancake
type of compressor used to build a deck. It's an oil less with only about
6 gal of capacity. I just checked it only draws 10 amps. While it wouldn't
be good for general building, it may be good enough to get you by in the
hangar.

--


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
Tim Olson



Joined: 25 Jan 2007
Posts: 2872

PostPosted: Wed Sep 24, 2008 3:20 am    Post subject: Air compressor tripping circuit breaker Reply with quote

That's a good way to go. I didn't mention in my post that I left
my nice high-flowing CH compressor at home because that's where
any hard building would be done, and I got a used Craftsman 20
or 25 gallon for the hangar. It's still bigger (and far far
noisier) than I need for the occasional hangar use. So yeah,
investing in a light duty compressor could be a quick way around
the problem too. Depends on if you plan to bring other tools,
like I bought a drill press, and a few other tools for the hangar
so I wouldn't have to bring mine from home. If you're just in
need of a little air, get the small compresor, but if you're trying
to build a little workshop, just have someone wire the place
the way you want.

Tim Olson - RV-10 N104CD - Flying
do not archive
Bob Leffler wrote:
[quote]

Before I was in the aircraft building business, I purchased a small pancake
type of compressor used to build a deck. It's an oil less with only about
6 gal of capacity. I just checked it only draws 10 amps. While it wouldn't
be good for general building, it may be good enough to get you by in the
hangar.

--


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
View user's profile Send private message Send e-mail
Deems Davis



Joined: 09 Jan 2006
Posts: 925

PostPosted: Wed Sep 24, 2008 4:54 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Thanks to all who provided suggestions, both on and off-line. My plan is:

1. check/service the old compressor (change oil and re- tension belt)
2. Investigate alternative power options with Airport maintenance. KDVT
is the busiest general aviation airport in the US and is owned and
operated by the City of Phoenix, they have a 3 year waiting list to get
into hangars , and set of rules that would choke a horse, enforced by
annual and periodic random inspections. All of which seems to have
turned the notion of being serice/servant to the public on it ear.
3. Obtain a light duty compressor for hangar use. And move 'Ol Reliable
back home.
Thanks

Deems

Quote:



- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
View user's profile Send private message Send e-mail
jkreidler



Joined: 13 Feb 2008
Posts: 151
Location: Sheboygan Falls WI

PostPosted: Wed Sep 24, 2008 5:06 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Deems, I spend my days engineering electric motors, so I can spend my nights building airplanes. I have also spent a bit of my career engineering air compressors.

A few things you could look at to help solve your problem. Check what sort of pressure switch your compressor has; the pressure switch may, or may not have a pressure bleed off built in. This is a device that releases the residual pressure in the compressor head, not in the tank. The purpose is to let the motor get a running start, instead of starting under immediate load. If you compressor 'hisses' when it shuts down, sorta like air brakes on a semi, then it is most likely already equipped with this device. You can sometimes also tell by looking for separate small airline leading to the switch. This is an easy retrofit, and adding such a switch could solve your problem, maybe.

From a motor standpoint, the motor could draw as much as seven times the rated full load amps at start up, in your case we are talking about 105amps, that is a big number!! There are different motor designs available to ease the starting current, check to see if the motor that is installed has two capacitors, one start cap (usually black), and a run cap (usually silver). If you only have one cap, you could change out the motor for a cap start, cap run type motor. This could also solve the problem. As was suggested before if you can get 220 voltage, it would most likely solve the problem all by itself. Just make sure you are getting two separate legs. Assuming this is a public place, you will most likely need to get a pro involved.

Keep in mind, I engineer the mechanical parts, this new found electrical stuff frightens and confuses me. Electricity is just a passing fad, like carpet, or automobiles.

Thanks, Jason Kreidler
4-Partner Build (Jason Kreidler, Tony Kolar, Kyle Hokel, Wayne Elsner)
Sheboygan Falls, WI
#40617 Finishing
Do Not Archive [quote][b]


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List

_________________
Jason Kreidler
4 Partner Build - Sheboygan Falls, WI
Tony Kolar, Kyle Hokel, Wayne Elser, Jason Kreidler
N44YH - Flying - #40617
Back to top
View user's profile Send private message
scottmschmidt(at)yahoo.co
Guest





PostPosted: Wed Sep 24, 2008 9:39 am    Post subject: Air compressor tripping circuit breaker Reply with quote

OK, all you EE majors weigh in here.

Do you know if you have more than one circuit in your hanger?
If so, buy a couple of plugs and wire them together in parallel, then into a female plug end.

I think this should give you 120 volts and 30 amps. Blast me if I'm wrong here.
This could be the cheapest solution.

If not, buy an oil less compressor. I run my Sears compressor on 15 amps all the time.

If you don't have two circuits steal one from the next door neighbor and just run an extension cord over to you place.

Scott Schmidtscottmschmidt(at)yahoo.com

---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
Deems Davis



Joined: 09 Jan 2006
Posts: 925

PostPosted: Wed Sep 24, 2008 10:18 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Well, Thanks to all for the suggestions. I made a trip to the hangar
this am. Jason, I found the compressor is equipped with all of the
features you mentioned (bleed valve & capacitors), I removed the belt
guard, and checked tension which appears 'normal' (?) then removed the
old (black) oil and replaced it with new compressor oil from Lowes, gave
it several turns of the flywheel manually to lubricate the cyls then
plugged it in directly to the outlet vs the extension cord and.........
Viola! it worked!!!!! no tripped circuit ?!?!? I should mention that
there were no other folks out in the adjacent hangars today. I checked
with airport nazis ops about the possibility of changing/modifying the
service........ I think they are still laughing, glad I could make their
day. They told me that there were up to 3 other hangars on the same
circuit, so who knows how long this will work, but it should suffice for
the intermittent needs for final assembly and maint at the hangar
Deems Davis
do not archive

Scott Schmidt wrote:
[quote] OK, all you EE majors weigh in here.

Do you know if you have more than one circuit in your hanger?
If so, buy a couple of plugs and wire them together in parallel, then
into a female plug end.

I think this should give you 120 volts and 30 amps. Blast me if I'm
wrong here.
This could be the cheapest solution.

If not, buy an oil less compressor. I run my Sears compressor on 15
amps all the time.

If you don't have two circuits steal one from the next door neighbor
and just run an extension cord over to you place.

Scott Schmidt
scottmschmidt(at)yahoo.com
---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
View user's profile Send private message Send e-mail
jcumins(at)jcis.net
Guest





PostPosted: Wed Sep 24, 2008 11:06 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Hey Deems

The Nut Tree airport in Northern California is the same way. There
maintenance man is like a little Hitler and will bust your chops on any rule
violation he can see or sniff out.

The hangers are privately or county owned with a set of rules that an
attorney very proud of. And no they do not allow any experimental building
in the hangers. A kit does not constitute a airplane, and it will not
qualify for a hanger, it must be a registered airworthy airplane to qualify
for a hanger. The waiting list is over 4 yrs now. So ya do everything ya
can to keep the hanger ya have.

John

40864 Rubber inprocess.

--


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
scottmschmidt(at)yahoo.co
Guest





PostPosted: Wed Sep 24, 2008 11:33 am    Post subject: Air compressor tripping circuit breaker Reply with quote

OK, here is the solution if your fix ever fails.
You just need to install the Rockwell automation device described in the video below and you will be in great shape.
I don't know why I didn't think of this sooner.

http://www.youtube.com/watch?v=TuhYd9L_d7w

Scott Schmidtscottmschmidt(at)yahoo.com

---


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
pitts_pilot(at)bellsouth.
Guest





PostPosted: Wed Sep 24, 2008 11:34 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Scott Schmidt wrote:
Quote:
OK, all you EE majors weigh in here.

Do you know if you have more than one circuit in your hanger?
If so, buy a couple of plugs and wire them together in parallel, then
into a female plug end.

I think this should give you 120 volts and 30 amps. Blast me if I'm
wrong here.
This could be the cheapest solution.
Well, this can get you hurt. Funny story. Might have been sad. My Dad

had need for higher current to his ham shack for his new linear. He
followed your same reasoning ..... just parallel them. His panel was
the old kind with two fuses (picture 3" long, 1/2" dia) in a block that
plugged into his panel. So, his idea was to wrap a piece of wire around
one end of the block, put the fuses back in and ..... I told him it
wouldn't work that way. Here it comes: "Of course it will, son!!!"
Well, I talked him into wrapping a towel around his hand (gloves would
have been better) but couldn't talk him our of his 'experiment'. The
noise when he plugged that into the panel was like a .45 going off close
by. Really loud in that garage!!!! The inside of the fuse block had
this nice copper finish to it. He still didn't understand what was
wrong with his ohms law logic ..... and there wasn't any. He shorted
the two legs of the 220 together. It's the simple mistakes that you pay
so dearly for.

Even if he had been successful, the wiring would still have been too
small, and could have resulted in fire. So, if you want to play
electrician, get some training first. If you're in a hurry ..... spend
the money on an electrician. You'll possibly save a whole bundle on
hospital bills ..... if you survive. I made my living guiding electrons
around, and the nasty b......s will turn and bite you in a heartbeat. I
just want you folks to be safe.

I'll bet that Rick has seen some pretty stupid stuff with his work .....
maybe he'll chime in.
Quote:

If not, buy an oil less compressor. I run my Sears compressor on 15
amps all the time.
It depends on just how far you are from the breaker box too. Buy one

where you know you can return it.
Quote:

If you don't have two circuits steal one from the next door neighbor
and just run an extension cord over to you place.
Again, you might be lucky ..... or you might let the magic smoke out.

Magic smoke will not work exposed to the atmosphere. Your best and
safest route is to get a buddy or electrician that's knowledgeable ....
and has the tools .... such as a meter ..... to help on this project.
Linn


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
pitts_pilot(at)bellsouth.
Guest





PostPosted: Wed Sep 24, 2008 11:45 am    Post subject: Air compressor tripping circuit breaker Reply with quote

Scott Schmidt wrote:
Quote:
OK, here is the solution if your fix ever fails.
You just need to install the Rockwell automation device described in
the video below and you will be in great shape.
I don't know why I didn't think of this sooner.

http://www.youtube.com/watch?v=TuhYd9L_d7w

Scott Schmidt
scottmschmidt(at)yahoo.com
Now, that's a hoot!!! Thanks for posting that ... I needed a good belly

laugh.
Wish I knew how to suck the youtube stuff into my archive of movies.
Linn
do not archive


- The Matronics RV10-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?RV10-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> RV10-List All times are GMT - 8 Hours
Goto page 1, 2  Next
Page 1 of 2

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group