PostPosted: Wed Nov 02, 2011 5:56 am    Post subject: E-Bus Circuit Protection Reply with quote

With an all electric panel (Cozy MkIV), my Essential Bus will pull ~22 amps with everthing on it running full blast. In real world ops with backup components powered off (ie Nav/Comm #2, etc.), it would be down to ~15 amps at night. Question 1: Is the B&C S8009 40A relay suitable to use for the alternate E-bus feed. Question 2: For circuit protection on the 10ga power feed from the Batt Bus to the E-Bus (via relay), can I splice into 2 of the 15amp fuse slots so as not to exceed the recommended load per slot or can I use a 14ga wire as a fuse-link coming off the main connection terminal of the Batt Bus fuse block?

Thanks,
William


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
William E. Buckley
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Wed Nov 02, 2011 2:07 pm    Post subject: E-Bus Circuit Protection Reply with quote

At 08:53 AM 11/2/2011, you wrote:
Quote:

<hoverandwire(at)yahoo.com>

With an all electric panel (Cozy MkIV), my Essential Bus will pull
~22 amps with everthing on it running full blast. In real world ops
with backup components powered off (ie Nav/Comm #2, etc.), it would
be down to ~15 amps at night. Question 1: Is the B&C S8009 40A relay
suitable to use for the alternate E-bus feed. Question 2: For
circuit protection on the 10ga power feed from the Batt Bus to the
E-Bus (via relay), can I splice into 2 of the 15amp fuse slots so as
not to exceed the recommended load per slot or can I use a 14ga wire
as a fuse-link coming off the main connection terminal of the Batt
Bus fuse block?

Sounds like your endurance bus has strayed from
the original design goals. What all do you have
attached to this bus? What size battery are you
flying? Did you configure based on any particular
Z-figure?
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Uncle



Joined: 04 Oct 2011
Posts: 10

PostPosted: Thu Nov 03, 2011 3:38 am    Post subject: E-Bus Circuit Protection Reply with quote

Bob,
The schematic is attached. Its mostly the Z-11 with Z-30 and Z-32 mixed in(dual battery and relay controlled E-bus). Two 16AH batteries. Not all the wire sizes and CB/fuse sizes have been filled in yet. Still a work in progress.

Thanks,
William
--- On Wed, 11/2/11, Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com> wrote:

Quote:
From: Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com>
Subject: Re: E-Bus Circuit Protection
To: aeroelectric-list(at)matronics.com
Date: Wednesday, November 2, 2011, 6:04 PM
--> AeroElectric-List message
posted by: "Robert L. Nuckolls, III" <nuckolls.bob(at)aeroelectric.com>

At 08:53 AM 11/2/2011, you wrote:
>
William <hoverandwire(at)yahoo.com>
>
> With an all electric panel (Cozy MkIV), my Essential
Bus will pull ~22 amps with everthing on it running full
blast. In real world ops with backup components powered off
(ie Nav/Comm #2, etc.), it would be down to ~15 amps at
night. Question 1: Is the B&C S8009 40A relay suitable
to use for the alternate E-bus feed. Question 2: For circuit
protection on the 10ga power feed from the Batt Bus to the
E-Bus (via relay), can I splice into 2 of the 15amp fuse
slots so as not to exceed the recommended load per slot or
can I use a 14ga wire as a fuse-link coming off the main
connection terminal of the Batt Bus fuse block?

  Sounds like your endurance bus has strayed from
  the original design goals. What all do you have
  attached to this bus? What size battery are you
  flying? Did you configure based on any particular
  Z-figure?


  Bob . . .

============

Quote:
Lists This Month --
Some AWESOME FREE Gifts!)
Raiser.  Click on
out more about
Gifts provided
AeroElectric www.aeroelectric.com
www.buildersbooks.com
              -Matt
Dralle, List Admin.
============

Quote:
AeroElectric-List Email Forum -
FAQ,
============

Quote:
   - MATRONICS WEB FORUMS -
============

Quote:
List Contribution Web Site -
              -Matt
Dralle, List Admin.
============

Quote:






- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List



Electric_System_1-2_(11-02-11).pdf
 Description:

Download
 Filename:  Electric_System_1-2_(11-02-11).pdf
 Filesize:  34.51 KB
 Downloaded:  490 Time(s)


_________________
William E. Buckley
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Nov 03, 2011 8:48 am    Post subject: E-Bus Circuit Protection Reply with quote

At 06:35 AM 11/3/2011, you wrote:
Quote:
Bob,
The schematic is attached. Its mostly the Z-11 with Z-30 and Z-32
mixed in(dual battery and relay controlled E-bus). Two 16AH
batteries. Not all the wire sizes and CB/fuse sizes have been filled
in yet. Still a work in progress.

Understand. Okay, let's look at your numbers.
What are the load-analysis numbers for items
on the e-bus?

Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Uncle



Joined: 04 Oct 2011
Posts: 10

PostPosted: Thu Nov 03, 2011 11:31 am    Post subject: E-Bus Circuit Protection Reply with quote

Most of these came from the components' docs, some from examples in the 'Connection', and a few are SWAG's. For the Nav/Comms I listed both at max load (ie transmitting). Its not realistic to transmit on both simultaneouly and in a battery only scenario one would be turned off anyway. However I want both to be available on the Ebus to allow for a really bad night if the alternator and one nav/comm quit. Perhaps it is overkill to list both nav/comms at max load for this exercise?? Also, the relays to power the Ebus are not listed. Here's the E-bus load list.

Trim: 0.3
Lft Fwd Kneeboard Lt: 0.1
L&R Fuel Probes: 0.04
Inst Panel Lts: 0.5
Panel Fld Lts: 0.25
Dynon D180: 1.6 (Can op on internal batt ~1hr)
Dynon D10A: 1.0 (Can op on internal batt ~1hr)
TruTrak T&B: 0.5
Audio Panel: 1.0
Nav/Comm 1: 5.0
Nav/Comm 2: 5.0
Xpndr: 1.6
Left Panel Cig Lighter: 0.75 (SWAG load for handheld backup GPS or other)
Fuel Boost/Prime: 1.5
Annunciator panel: 1.5 (8 LED's with controlling circuit module)

--- On Thu, 11/3/11, Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com> wrote:

Quote:
From: Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com>
Subject: Re: Fw: Re: E-Bus Circuit Protection
To: aeroelectric-list(at)matronics.com
Date: Thursday, November 3, 2011, 12:46 PM
--> AeroElectric-List message
posted by: "Robert L. Nuckolls, III" <nuckolls.bob(at)aeroelectric.com>

At 06:35 AM 11/3/2011, you wrote:
> Bob,
> The schematic is attached. Its mostly the Z-11 with
Z-30 and Z-32 mixed in(dual battery and relay controlled
E-bus). Two 16AH batteries. Not all the wire sizes and
CB/fuse sizes have been filled in yet. Still a work in
progress.

  Understand. Okay, let's look at your numbers.
  What are the load-analysis numbers for items
  on the e-bus?



  Bob . . .

Lists This Month --
Some AWESOME FREE Gifts!)
Raiser.  Click on
out more about
Gifts provided
AeroElectric www.aeroelectric.com
www.buildersbooks.com
              -Matt
Dralle, List Admin.
AeroElectric-List Email Forum -
FAQ,
   - MATRONICS WEB FORUMS -
List Contribution Web Site -
              -Matt
Dralle, List Admin.






- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
William E. Buckley
Back to top
View user's profile Send private message
user9253



Joined: 28 Mar 2008
Posts: 1922
Location: Riley TWP Michigan

PostPosted: Fri Nov 04, 2011 6:08 am    Post subject: Re: E-Bus Circuit Protection Reply with quote

Question 1: Yes, the B&C S8009 40A relay is be suitable, IMHO.
Question 2: For circuit protection, it not advisable to parallel fuses.

One of the Dynons and one of the nav/coms can be moved to the main power bus.
The estimated current draw of some of the loads seems to be on the high side. The Garmin GTX-327 typically uses about 1.1 amps, a nav/com about 1 amp receive and 3 amps transmit, depending on the brand.
If some of the load is moved to the main bus, the load on the e-bus will drop to under 10 amps and can be protected with a 15 amp fuse fed with 14AWG.
The 4AWG feeding the main power bus could be downsized to #6 unless it is a long run. 8AWG could even be used for very short runs. Even though the alternator is rated for 60 amps, it will normally be putting out a fraction of that.
The ammeter shunt location will show battery charging current which is normally close to zero, pretty useless information. System voltage will indicate if the alternator is working or not. You might consider eliminating the shunt and using that Dynon D-180 screen space for displaying some other more useful parameter, perhaps temperature from a thermocouple.
Joe


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Joe Gores
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Fri Nov 04, 2011 8:18 am    Post subject: E-Bus Circuit Protection Reply with quote

At 02:26 PM 11/3/2011, you wrote:

<hoverandwire(at)yahoo.com>

Most of these came from the components' docs, some from examples in
the 'Connection', and a few are SWAG's. For the Nav/Comms I listed
both at max load (ie transmitting). Its not realistic to transmit on
both simultaneouly and in a battery only scenario one would be turned
off anyway. However I want both to be available on the Ebus to allow
for a really bad night if the alternator and one nav/comm quit.
Perhaps it is overkill to list both nav/comms at max load for this
exercise?? Also, the relays to power the Ebus are not listed. Here's
the E-bus load list.

Okay, Joe beat me to it with some astute observatation
cogent arguments. I'll expand on Joe's posting as follows:

Trim: 0.3 (This is an intermittant load not significant
to an energy study)
Lft Fwd Kneeboard Lt: 0.1
L&R Fuel Probes: 0.04
Inst Panel Lts: 0.5
Panel Fld Lts: 0.25 (Do you need BOTH lighting systems in a
endurance mode?)
Dynon D180: 1.6
Dynon D10A: 1.0
TruTrak T&B: 0.5 (Are all of these instruments part of your
Plan-B for alternator-out operations? It appears
that the D180 has the broadest range of features
and could be the e-bus favorite for alternator-out
ops)
Audio Panel: 1.0
Nav/Comm 1: 5.0
Nav/Comm 2: 5.0 (Surely one nav/com would suffice. Further, while
the peak load may be 5A during transmit, only
the receive mode is significant to the total
energy requirements)
Xpndr: 1.6
Left Panel Cig Lighter: 0.75 (SWAG load for handheld backup GPS or other)
(Do you have a MAIN GPS?)

Fuel Boost/Prime: 1.5 (also intermittent duty)

Annunciator panel: 1.5 (8 LED's with controlling circuit module)
(This is a LOT of of current for an LED annunciator)

I think if you consider the normal running loads
upon which you stack the occasional transient load
your total load figures will get much better.

Have you considered the SD-8 as an aux alternator
to support alternator out ops? What's your calculated
endurance, battery only?)

------------- Joe's Response with further food for thought
----------------------
At 09:08 AM 11/4/2011, you wrote:


Question 1: Yes, the B&C S8009 40A relay is be suitable, IMHO.
Question 2: For circuit protection, it not advisable to parallel fuses.

One of the Dynons and one of the nav/coms can be moved to the main power bus.
The estimated current draw of some of the loads seems to be on the
high side. The Garmin GTX-327 typically uses about 1.1 amps, a
nav/com about 1 amp receive and 3 amps transmit, depending on the brand.
If some of the load is moved to the main bus, the load on the
e-bus will drop to under 10 amps and can be protected with a 15 amp
fuse fed with 14AWG.
The 4AWG feeding the main power bus could be downsized to #6
unless it is a long run. 8AWG could even be used for very short
runs. Even though the alternator is rated for 60 amps, it will
normally be putting out a fraction of that.
The ammeter shunt location will show battery charging current
which is normally close to zero, pretty useless information. System
voltage will indicate if the alternator is working or not. You might
consider eliminating the shunt and using that Dynon D-180 screen
space for displaying some other more useful parameter, perhaps
temperature from a thermocouple.
Joe

--------
Joe Gores


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Uncle



Joined: 04 Oct 2011
Posts: 10

PostPosted: Fri Nov 04, 2011 11:21 am    Post subject: E-Bus Circuit Protection Reply with quote

Gents,
Feedback very much appreciate. A bit more work to do on my end. Circling back to one of the original questions: for circuit protect of the ebus supply line, any harm in doing it with a fusible-link (14ga for 10ga supply)?

William

--- On Fri, 11/4/11, Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com> wrote:

Quote:
From: Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com>
Subject: Re: Fw: Re: Fw: Re: E-Bus Circuit Protection
To: aeroelectric-list(at)matronics.com
Date: Friday, November 4, 2011, 12:13 PM
--> AeroElectric-List message
posted by: "Robert L. Nuckolls, III" <nuckolls.bob(at)aeroelectric.com>

At 02:26 PM 11/3/2011, you wrote:

<hoverandwire(at)yahoo.com>

Most of these came from the components' docs, some from
examples in the 'Connection', and a few are SWAG's. For the
Nav/Comms I listed both at max load (ie transmitting). Its
not realistic to transmit on both simultaneouly and in a
battery only scenario one would be turned off anyway.
However I want both to be available on the Ebus to allow for
a really bad night if the alternator and one nav/comm quit.
Perhaps it is overkill to list both nav/comms at max load
for this exercise?? Also, the relays to power the Ebus are
not listed. Here's the E-bus load list.

     Okay, Joe beat me to it with some
astute observatation
     cogent arguments. I'll expand on
Joe's posting as follows:

Trim: 0.3    (This is an intermittant load not
significant
              to an
energy study)
Lft Fwd Kneeboard Lt: 0.1
L&R Fuel Probes: 0.04
Inst Panel Lts: 0.5
Panel Fld Lts: 0.25  (Do you need BOTH lighting
systems in a
               
      endurance mode?)
Dynon D180: 1.6
Dynon D10A: 1.0
TruTrak T&B: 0.5     (Are all of
these instruments part of your
               
      Plan-B for alternator-out operations?
It appears
               
      that the D180 has the broadest range of
features
               
      and could be the e-bus favorite for
alternator-out
               
      ops)
Audio Panel: 1.0
Nav/Comm 1: 5.0
Nav/Comm 2: 5.0      (Surely one nav/com
would suffice. Further, while
               
      the peak load may be 5A during
transmit, only
               
      the receive mode is significant to the
total
               
      energy requirements)
Xpndr: 1.6
Left Panel Cig Lighter: 0.75 (SWAG load for handheld backup
GPS or other)
               
     (Do you have a MAIN GPS?)

Fuel Boost/Prime: 1.5  (also intermittent duty)

Annunciator panel: 1.5 (8 LED's with controlling circuit
module)
               
      (This is a LOT of of current for an LED
annunciator)

               
    I think if you consider the normal running
loads
               
    upon which you stack the occasional transient
load
               
    your total load figures will get much better.

               
    Have you considered the SD-8 as an aux
alternator
               
    to support alternator out ops?  What's
your calculated
               
    endurance, battery only?)

------------- Joe's Response with further food for thought
----------------------
At 09:08 AM 11/4/2011, you wrote:

<fran4sew(at)banyanol.com>

Question 1: Yes, the B&C S8009 40A relay is be
suitable, IMHO.
Question 2: For circuit protection, it not advisable to
parallel fuses.

One of the Dynons and one of the nav/coms can be moved to
the main power bus.
The estimated current draw of some of the loads seems to be
on the high side.  The Garmin GTX-327 typically uses
about 1.1 amps, a nav/com about 1 amp receive and 3 amps
transmit, depending on the brand.
  If some of the load is moved to the main bus, the
load on the e-bus will drop to under 10 amps and can be
protected with a 15 amp fuse fed with 14AWG.
  The 4AWG feeding the main power bus could be
downsized to #6 unless it is a long run.  8AWG could
even be used for very short runs.  Even though the
alternator is rated for 60 amps, it will normally be putting
out a fraction of that.
  The ammeter shunt location will show battery
charging current which is normally close to zero, pretty
useless information.  System voltage will indicate if
the alternator is working or not.  You might consider
eliminating the shunt and using that Dynon D-180 screen
space for displaying some other more useful parameter,
perhaps temperature from a thermocouple.
Joe

--------
Joe Gores



Lists This Month --
Some AWESOME FREE Gifts!)
Raiser.  Click on
out more about
Gifts provided
AeroElectric www.aeroelectric.com
www.buildersbooks.com
              -Matt
Dralle, List Admin.
AeroElectric-List Email Forum -
FAQ,
   - MATRONICS WEB FORUMS -
List Contribution Web Site -
              -Matt
Dralle, List Admin.






- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
William E. Buckley
Back to top
View user's profile Send private message
user9253



Joined: 28 Mar 2008
Posts: 1922
Location: Riley TWP Michigan

PostPosted: Fri Nov 04, 2011 3:26 pm    Post subject: Re: E-Bus Circuit Protection Reply with quote

Quote:
Okay, Joe beat me to it with some astute observatation cogent arguments.

You deserve the credit, Bob, for being my mentor.
Joe


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
Joe Gores
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Fri Nov 04, 2011 9:46 pm    Post subject: E-Bus Circuit Protection Reply with quote

At 02:18 PM 11/4/2011, you wrote:
Quote:

<hoverandwire(at)yahoo.com>

Gents,
Feedback very much appreciate. A bit more work to do on my end.
Circling back to one of the original questions: for circuit protect
of the ebus supply line, any harm in doing it with a fusible-link
(14ga for 10ga supply)?

William

Not recommended. Fusible links (like current limiters)
are intended to protect HEAVY feeders subject to large,
short time transients (like downstream breaker trips).

There's no sin in fusing a wire for less than rated
capability. I've often used upsized wires to get a lower
voltage drop . . . without upsizing the protection.

If your goal is to embrace the original design goals
for the e-bus, then total loads need to be reduced to
some value that affords HOURS of endurance battery
only. What size batteries do you plan to carry?
Just as an example:

http://www.aeroelectric.com/Pictures/Curves/17AH_12V_Capacity_vs_Load.gif

This set of performance curves for an 18 a.h. battery
suggest that a NEW battery will carry a 5 amp e-bus
for 2 hours. If you need that 2 hour goal to be met
at an 80% end of service life, then you'd need to
downsize to about 4 amps e-bus load.

Your batteries need to be selected as a trade-off
between equipment really necessary for comfortable
en route operations and the amount of lead and
plastic you're willing to drag around. This study
in energy management illustrates the value in adding
the SD-8 standby alternator. It's good for 8A for
ANY number of hours thus saving limited energy
in SMALLER batteries for approach to landing
and arrival. That 3.5 pound alternator can replace
a whole lot more pounds of lead.

One battery and two alternators is a lot more
attractive than one alternator and any number/size
of batteries.
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Uncle



Joined: 04 Oct 2011
Posts: 10

PostPosted: Sat Nov 05, 2011 4:09 am    Post subject: E-Bus Circuit Protection Reply with quote

Good info. Thanks for the extra help.

William

--- On Sat, 11/5/11, Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com> wrote:

Quote:
From: Robert L. Nuckolls, III <nuckolls.bob(at)aeroelectric.com>
Subject: Re: E-Bus Circuit Protection
To: aeroelectric-list(at)matronics.com
Date: Saturday, November 5, 2011, 1:42 AM
--> AeroElectric-List message
posted by: "Robert L. Nuckolls, III" <nuckolls.bob(at)aeroelectric.com>

At 02:18 PM 11/4/2011, you wrote:
>
William <hoverandwire(at)yahoo.com>
>
> Gents,
> Feedback very much appreciate. A bit more work to do
on my end. Circling back to one of the original questions:
for circuit protect of the ebus supply line, any harm in
doing it with a fusible-link (14ga for 10ga supply)?
>
> William

  Not recommended. Fusible links (like current
limiters)
  are intended to protect HEAVY feeders subject to
large,
  short time transients (like downstream breaker
trips).

  There's no sin in fusing a wire for less than rated
  capability. I've often used upsized wires to get a
lower
  voltage drop . . . without upsizing the protection.

  If your goal is to embrace the original design
goals
  for the e-bus, then total loads need to be reduced
to
  some value that affords HOURS of endurance battery
  only. What size batteries do you plan to carry?
  Just as an example:

http://www.aeroelectric.com/Pictures/Curves/17AH_12V_Capacity_vs_Load.gif

  This set of performance curves for an 18 a.h.
battery
  suggest that a NEW battery will carry a 5 amp e-bus
  for 2 hours. If you need that 2 hour goal to be met
  at an 80% end of service life, then you'd need to
  downsize to about 4 amps e-bus load.

  Your batteries need to be selected as a trade-off
  between equipment really necessary for comfortable
  en route operations and the amount of lead and
  plastic you're willing to drag around. This study
  in energy management illustrates the value in
adding
  the SD-8 standby alternator. It's good for 8A for
  ANY number of hours thus saving limited energy
  in SMALLER batteries for approach to landing
  and arrival. That 3.5 pound alternator can replace
  a whole lot more pounds of lead.

  One battery and two alternators is a lot more
  attractive than one alternator and any number/size
  of batteries.


  Bob . . .

Lists This Month --
Some AWESOME FREE Gifts!)
Raiser.  Click on
out more about
Gifts provided
AeroElectric www.aeroelectric.com
www.buildersbooks.com
              -Matt
Dralle, List Admin.
AeroElectric-List Email Forum -
FAQ,
   - MATRONICS WEB FORUMS -
List Contribution Web Site -
              -Matt
Dralle, List Admin.






- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List

_________________
William E. Buckley
Back to top
View user's profile Send private message
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group