PostPosted: Sun Jun 04, 2006 8:31 am    Post subject: Drills and wiring Reply with quote

All-   
    The second battery pack was no good from the get-go. Wouldn't charge. 
    So, another trip to Home Depot to exchange for a new drill. I told them I'd give the Ridgid one more chance, but even if I did have a lifetime warranty, I couldn't keep blowing half my weekend returning drills instead of using them. Any more problems and I'm still in the market for something reliable.
    I did get to install a couple of shop light circuits with the good battery, and the drill performance (Compared to my old Craftsman) is awesome. Hope there are no more problems. Update- both packs charged this time.
    Incidentally, I looked for the models recommended by listers, but there are no local stores that handle them. As always, thanks for the input.
    Question for the electricians out there- My big power tools are a drill press, metal band saw, table saw, and belt/disc sander. I plan on adding a wood band saw and Lincoln 240V stick welder down the line.
    I installed a sub breaker panel from the main and have a 30A 240V circuit for the welder, 2-20A GFCI protected outlet circuits, and a 20A lighting circuit all connected with 12/2 w/ground. Outlets are double gang every 4', and 4' shop lights are every 6'. Can I quit now? I have space in the main box left for 1-30A 240 or 2-15A 120 breakers if need be.
    Please say I'm done! The price of Romex has gone up .30/ft in the past two weeks!!!!
                                                                    Bill
                                    do not archive 
   
   


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
TH-SR



Joined: 13 Jan 2006
Posts: 22
Location: WI

PostPosted: Sun Jun 04, 2006 8:46 am    Post subject: Drills and wiring Reply with quote

Bill,
30A for the welder sounds kind of light - I have a 50A circuit for mine...
Todd
Do Not Archive 

From: owner-zenith-list-server(at)matronics.com [mailto:owner-zenith-list-server(at)matronics.com] On Behalf Of Bill Naumuk
Sent: Sunday, June 04, 2006 11:30 AM
To: zenith list
Subject: Drills and wiring

All-   
    The second battery pack was no good from the get-go. Wouldn't charge. 
    So, another trip to Home Depot to exchange for a new drill. I told them I'd give the Ridgid one more chance, but even if I did have a lifetime warranty, I couldn't keep blowing half my weekend returning drills instead of using them. Any more problems and I'm still in the market for something reliable.
    I did get to install a couple of shop light circuits with the good battery, and the drill performance (Compared to my old Craftsman) is awesome. Hope there are no more problems. Update- both packs charged this time.
    Incidentally, I looked for the models recommended by listers, but there are no local stores that handle them. As always, thanks for the input.
    Question for the electricians out there- My big power tools are a drill press, metal band saw, table saw, and belt/disc sander. I plan on adding a wood band saw and Lincoln 240V stick welder down the line.
    I installed a sub breaker panel from the main and have a 30A 240V circuit for the welder, 2-20A GFCI protected outlet circuits, and a 20A lighting circuit all connected with 12/2 w/ground. Outlets are double gang every 4', and 4' shop lights are every 6'. Can I quit now? I have space in the main box left for 1-30A 240 or 2-15A 120 breakers if need be.
    Please say I'm done! The price of Romex has gone up .30/ft in the past two weeks!!!!
                                                                    Bill
                                    do not archive 
   
   


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List

_________________
Todd
CH701
Back to top
View user's profile Send private message
naumuk(at)alltel.net
Guest





PostPosted: Sun Jun 04, 2006 1:33 pm    Post subject: Drills and wiring Reply with quote

Todd-
    Depends on the welder. Just talked to my uncle, who owns the same basic model as I'm considering. He does it on a 20A circuit.
    New drill doesn't seem as fast as the last on the first battery. I'll swap them and see if there's a difference. 
    Don't you love the price of Romex!? Should have bought copper futures!
                                                                    Bill
                                   do not archive
[quote] ---


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
bryanmmartin



Joined: 10 Jan 2006
Posts: 1018

PostPosted: Sun Jun 04, 2006 2:03 pm    Post subject: Drills and wiring Reply with quote

You don't have that 30A welder circuit wired with 12 gauge wire do
you? It should be wired with 10 gauge wire. Other than that your
setup looks good as long as you're not going to be running multiple
loads simultaneously on the same circuit.

On Jun 4, 2006, at 12:29 PM, Bill Naumuk wrote:

Quote:
I installed a sub breaker panel from the main and have a 30A
240V circuit for the welder, 2-20A GFCI protected outlet circuits,
and a 20A lighting circuit all connected with 12/2 w/ground.
Outlets are double gang every 4', and 4' shop lights are every 6'.
Can I quit now? I have space in the main box left for 1-30A 240 or
2-15A 120 breakers if need be.
Please say I'm done! The price of Romex has gone up .30/ft in
the past two weeks!!!!

Bill
do not archive


--
Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List

_________________
--
Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.
Back to top
View user's profile Send private message
naumuk(at)alltel.net
Guest





PostPosted: Mon Jun 05, 2006 2:50 pm    Post subject: Drills and wiring Reply with quote

Bryan-
You hit on the one real question mark I had for the layout, and to tell
the truth, I'm puzzled.
I've had my work in the house inspected for insurance purposes twice
over the years, and the only places I was required to use 10g was for the
water heater and water pump. I have heaters in both my bathrooms wired with
12g that have never had a problem (I built the house in '8Cool and neither
inspector said a thing about them either time. Everyone I've talked to
around here said, yeah, you've got it right for the welder circuit.
I'm getting 234V at the box, and the outlet is only 2' away. If my
lights dim drastically, or I pop a breaker, I'll know why and go with 10g.
As far as the rest of the circuits, I can only run one tool at a time!


Bill
do
not archive
---


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
p.mulwitz(at)worldnet.att
Guest





PostPosted: Mon Jun 05, 2006 3:29 pm    Post subject: Drills and wiring Reply with quote

At 03:45 PM 6/5/2006, you wrote:
Quote:
If my lights dim drastically, or I pop a breaker, I'll know why and
go with 10g.


Bill,

The issue for what wire size to use is not voltage droop or circuit
breaker action. It is the temperature rise in the wire as a result
of the current. I don't know the building codes, but the standard
used in electronic equipment design limits temperature rise to 10
degrees Celsius. If you let the wires get really hot there is a risk of fire.

Have fun,

Paul
XL wings
do not archive
---------------------------------------------
Paul Mulwitz
32013 NE Dial Road
Camas, WA 98607
---------------------------------------------


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
bryanmmartin



Joined: 10 Jan 2006
Posts: 1018

PostPosted: Mon Jun 05, 2006 3:51 pm    Post subject: Drills and wiring Reply with quote

In most cases, a 30 amp circuit must be wired with 10 gauge wire. But
after further research in the NEC, I see that welder circuits are an
exception to the rule. Article 630 allows the size of the conductor
to be reduced according to the duty cycle of the welder, so your
circuit is probably correct.

The voltage of the circuit is irrelevent, the current rating of the
load is the important factor. The circuit breaker is usually sized to
protect the wire in the circuit from overheating due to too much
current flow.
Your 240 volt electric space heaters are probably rated at less than
16 Amps which would allow a 20 Amp breaker and 12 guage wire.

I used to be an electrician but I haven't worked in that field for
several years so some of this stuff has faded from memory.

On Jun 5, 2006, at 6:45 PM, Bill Naumuk wrote:

Quote:


Bryan-
You hit on the one real question mark I had for the layout, and
to tell the truth, I'm puzzled.
I've had my work in the house inspected for insurance purposes
twice over the years, and the only places I was required to use 10g
was for the water heater and water pump. I have heaters in both my
bathrooms wired with 12g that have never had a problem (I built the
house in '8Cool and neither inspector said a thing about them either
time. Everyone I've talked to around here said, yeah, you've got it
right for the welder circuit.
I'm getting 234V at the box, and the outlet is only 2' away. If
my lights dim drastically, or I pop a breaker, I'll know why and go
with 10g.
As far as the rest of the circuits, I can only run one tool at a
time!


Bill

--
Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List

_________________
--
Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.
Back to top
View user's profile Send private message
601zv(at)ritternet.com
Guest





PostPosted: Mon Jun 05, 2006 4:18 pm    Post subject: Drills and wiring Reply with quote

While the whole shop is burning down and melting everyting in it you will
briefly have plenty of light while you consider the choice of using an
oversized breaker with undersized wire, and may develop a new perspective on
dim lights.

Do not archive.
---


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
bryanmmartin



Joined: 10 Jan 2006
Posts: 1018

PostPosted: Mon Jun 05, 2006 4:31 pm    Post subject: Drills and wiring Reply with quote

The primary reason for a choosing a particular wire size is to
prevent overheating due to current. But for long wire runs, voltage
drop also becomes a factor, the wires should be sized to prevent a
voltage drop of more than 3% at the farthest end of a branch circuit.
If you don't follow this guide, you won't cause your lights to dim or
circuit breakers to pop, your load will just run at under its rated
voltage. For a motor circuit, this can be a problem as motors don't
like running under speed. This is one reason major appliances can be
damaged during a "brown-out". If you've ever run a large drill motor
at the end of a long extension cord, you may have encountered this
situation. A 50 foot extension cord will be rated at a lower current
than a ten foot cord even if both use the same size wire.

On Jun 5, 2006, at 7:28 PM, Paul Mulwitz wrote:

Quote:

<p.mulwitz(at)worldnet.att.net>

At 03:45 PM 6/5/2006, you wrote:
> If my lights dim drastically, or I pop a breaker, I'll know why
> and go with 10g.
Bill,

The issue for what wire size to use is not voltage droop or circuit
breaker action. It is the temperature rise in the wire as a result
of the current. I don't know the building codes, but the standard
used in electronic equipment design limits temperature rise to 10
degrees Celsius. If you let the wires get really hot there is a
risk of fire.

Have fun,

Paul
XL wings
do not archive

--

Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List

_________________
--
Bryan Martin
N61BM, CH 601 XL, Stratus Subaru.
do not archive.
Back to top
View user's profile Send private message
jsimons2



Joined: 26 May 2006
Posts: 19
Location: Burlington, NC

PostPosted: Mon Jun 05, 2006 5:16 pm    Post subject: Re: Drills and wiring Reply with quote

Go with the 10 gauge wire and be safe. Most welders require a 30 amp circuit due to their current draw. The only time that #12 gauge wire is allowed to be on a circuit that is protected by more than a 20 amp breaker is on A/C and refridgeration equipment. It is then limited to no more than 25 amps minimum circuit ampacity. This is due to the high, but short duration, startup draw of compressors. No wire is allowed more than 80% of its rating for continuous load. The other receptacle circuits should be fine due to the fact that you will probably never use more than one piece of equipment at a time. All of my info comes straight from the NEC (National Electrical Code). My qualifications?? Senior electrical inspector for the city where I live and over 28 years in the business.

Jerome Simons
very near future 601 HDS scrap builder


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
View user's profile Send private message
naumuk(at)alltel.net
Guest





PostPosted: Tue Jun 06, 2006 2:36 pm    Post subject: Drills and wiring Reply with quote

Gotta love a scrap builder! Thanks.
Bill
do not archive
---


- The Matronics Zenith-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?Zenith-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> Zenith-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group