Valin



Joined: 13 Apr 2010
Posts: 31
Location: Colorado

PostPosted: Mon May 18, 2015 11:39 am    Post subject: Thermocouple Wire Connections Reply with quote

Hello,

We're on the verge of connecting our Garmin GEA 24 Engine Airframe Processor/Box to our engine's thermocouples. Each engine thermocouple has a pigtail of two wires with ring terminals on them. My question is, do we have to use the ring terminals to make the connection to our thermocouple wires running from the GEA 24?

I know the thermocouple temperature measurement is all about the electrical resistance being observed so I assume one needs as low a resistance connection as possible for best accuracy. Maybe two ring terminals held together with a screw/nut is the best -- but, wondering if knife type connections or something else would be as good...?

Thanks,

Valin
Lancair Legacy Project
Colorado

Sent by iPhone


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message Send e-mail
recapen(at)earthlink.net
Guest





PostPosted: Mon May 18, 2015 12:06 pm    Post subject: Thermocouple Wire Connections Reply with quote

There's plenty in the archives on this one....

As long as both sides of the connector are on the same side of the firewall and physically tight, you should be OK. The trick is that the actual wire has almost no elasticity to it so relying on a crimp connection is the weak point. I have experience with this in the first few hours - after that...I used the method suggested by the avionics manufacturer.....crimp plus solder quick disconnects with insulation
to keep the poles apart. Happy now after a couple hundred hours on it.....

--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
stein(at)steinair.com
Guest





PostPosted: Mon May 18, 2015 12:15 pm    Post subject: Thermocouple Wire Connections Reply with quote

Those connections aren't necessarily as important as having them all
consistently the same (whether it be ring terminals, butt-splices, knife
splices, pins, or whatever). Sure there will be increased resistance at
that junction, but if they are all uniform you won't see an unequal result.

Cheers,
Stein


--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Valin



Joined: 13 Apr 2010
Posts: 31
Location: Colorado

PostPosted: Mon May 18, 2015 1:48 pm    Post subject: Thermocouple Wire Connections Reply with quote

Thanks guys.

Stein, I see where it's okay as long as each temp probe has the same bias for EGTs. Seems like I'd want the CHTs to be as accurate as possible, though... Is there a best connection type for accuracy?

Thanks,

Valin

Sent by iPhone

[quote] On May 18, 2015, at 2:14 PM, Stein Bruch <stein(at)steinair.com> wrote:



Those connections aren't necessarily as important as having them all
consistently the same (whether it be ring terminals, butt-splices, knife
splices, pins, or whatever). Sure there will be increased resistance at
that junction, but if they are all uniform you won't see an unequal result.

Cheers,
Stein




--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message Send e-mail
millner(at)me.com
Guest





PostPosted: Mon May 18, 2015 2:09 pm    Post subject: Thermocouple Wire Connections Reply with quote

On 5/18/2015 12:38 PM, Valin & Allyson Thorn wrote:
Quote:
I know the thermocouple temperature measurement is all about the electrical resistance being observed
Not really... the input is high impedance, so a little resistance in the

connectors is not a big deal. The big deal is not extending the wire
with non-thermocouple wire, as that would introduce two cold
junctions... one at the terminals on the thermocouple, and the other at
the other end of the (presumably) copper extension wire. If one end is
cooler than the other, you'll modify the observed TC reading.

Any connector should work; the voltages are small, though, in the
millivolt range. But as long as the two ends of your connection pair are
at the same temperature, you're not introducing an error.

Paul


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
kjashton(at)vnet.net
Guest





PostPosted: Mon May 18, 2015 2:25 pm    Post subject: Thermocouple Wire Connections Reply with quote

Omega.com sells a line of connectors for thermocouple wires but i agree with Stein. If the connections are made in the same area of temperature, the errors are negligible. I have owned a Cozy that used ordinary copper wire between the thermocouples and the gauges up front. Seemed to work pretty well. I use thermocouple wire (type J or K) all the way on the two airplanes i built but i am not sure it really makes much difference over copper wires.

After fiddling with ring-terminal connections, I would just solder the connections and leave a little extra wire so you can just cut the connection if you need to pull the engine.
-kent

[quote] On May 18, 2015, at 5:46 PM, Valin & Allyson Thorn <thorn(at)starflight.aero> wrote:



Thanks guys.

Stein, I see where it's okay as long as each temp probe has the same bias for EGTs. Seems like I'd want the CHTs to be as accurate as possible, though... Is there a best connection type for accuracy?

Thanks,

Valin



Sent by iPhone

> On May 18, 2015, at 2:14 PM, Stein Bruch <stein(at)steinair.com> wrote:
>
>
>
> Those connections aren't necessarily as important as having them all
> consistently the same (whether it be ring terminals, butt-splices, knife
> splices, pins, or whatever). Sure there will be increased resistance at
> that junction, but if they are all uniform you won't see an unequal result.
>
> Cheers,
> Stein
>
>
>
>
> --


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
nuckolls.bob(at)aeroelect
Guest





PostPosted: Mon May 18, 2015 3:31 pm    Post subject: Thermocouple Wire Connections Reply with quote

At 03:14 PM 5/18/2015, you wrote:
--> AeroElectric-List message posted by: "Stein Bruch" <stein(at)steinair.com>

Those connections aren't necessarily as important as having them all
consistently the same (whether it be ring terminals, butt-splices, knife
splices, pins, or whatever). Sure there will be increased resistance at
that junction, but if they are all uniform you won't see an unequal result.


Exactly . . .

Somebody once opined that what was good for the
goose was also good for the gander. In this instance,
what's good for the chromel is good for the alumel.

In other words, how ever you splice the wires, the
path of electrons across metalic joints in one wire should
be equal and opposite those on the other wire. While
this still creates tiny errors, they're largely
cancelling and insignificant to system operations.

For more details, see:

www.aeroelectric.com/articles/excerpt.pdf



Bob . . . [quote][b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
millner(at)me.com
Guest





PostPosted: Tue May 19, 2015 6:19 am    Post subject: Thermocouple Wire Connections Reply with quote

Well, it subtracts the difference across the copper wire from your
readings... so as long as accuracy of your CHT numbers isn't important,
plus or minus 50 degrees, I guess that's OK...

Paul

On 5/18/2015 3:21 PM, Kent or Jackie Ashton wrote:
Quote:
i am not sure it really makes much difference over copper wires.


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Valin



Joined: 13 Apr 2010
Posts: 31
Location: Colorado

PostPosted: Tue May 19, 2015 9:56 am    Post subject: Re: Thermocouple Wire Connections Reply with quote

Thanks everyone and especially Bob and the article you wrote on thermocouples. I learned I didn't have a complete and accurate understanding of thermocouples and their principles.

We are connecting to the thermocouples with thermocouple wires. We already have the tiny ring terminals, screws, and nuts so might just go ahead and use them to connect to each thermocouple's pig tail wires that already have ring terminals on them.

Thanks again!

Valin


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message Send e-mail
millner(at)me.com
Guest





PostPosted: Thu May 21, 2015 2:00 pm    Post subject: Thermocouple Wire Connections Reply with quote

>> Explain, plz, difference of what? How do you arrive at plus or minus
50 degrees? Just interested in how you got to that much variation.

Each junction between different types of wire registers a voltage
difference... that's how thermocouples work.

Our aircraft thermocouples are typically chromel-alumel (exception is
CHTs for Insight GEM which are iron-constantine. Almost everyone else
uses only chromel-alumel)

If you use copper wire to extend a lead, then you make two junctions
near the engine, chromel-copper and alumel-copper. And you make two
junctions near the instrument, same pairings.

If the end near the engine is 50 degrees warmer than the end near the
instrument, not uncommon, then you introduce a net voltage change...
'cause the chromel - copper - chromel won't cancel out due to the
temperature difference. This is *unlike* the earlier discussion of
dissimilar metal connectors; there both ends of the connector are pretty
much the same temperature.

The voltage change and error is proportional to the temperature
difference between the uncompensated junctions (chromel-copper-chromel
and alumel-copper-alumel). It's not directly proportionate, 'cause the
thermocouple effect is non-linear; but for this kind of differences,
it's close enough to linear to estimate fairly accurately.

Paul


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group