nuckolls.bob(at)cox.net
Guest





PostPosted: Thu Oct 11, 2007 5:12 am    Post subject: [Probable SPAM] Z-19 E Bus feeder questions - Fuse select Reply with quote

At 02:15 PM 10/10/2007 -0400, you wrote:

Quote:


Mike,
I'll wait for the Bob's definitive answer but this makes no
sense. That would be like adding a 100 am panel to your home and feeding
it off a 20 amp breaker in your main panel.

The lead from the main power bus to the endurance bus should be
a direct feed from the same terminal as the main feed. Between them is a
diode to prevent backflow if the e-bus alternate is used.

Also, I have an issue with the orphaned switch for fuel pump #2.
Why not integrate it with the engine primary and secondary switching?
Note that if fuel pump #1 makes trouble, this diagram provides no way to
isolate it, but rather one method to switch the bus that feeds it. With
switch #2 I can turn it off/on at will which is fine as a backup, but I
want that functionality for #1 also.

Wondering what you're referring to here. The Z-19 as published
was for a specific engine and fuel system that offered only
1 ECU and 1 fuel pump. See:

http://www.aeroelectric.com/PPS/Adobe_Architecture_Pdfs/Z19M_1.pdf

http://www.aeroelectric.com/PPS/Adobe_Architecture_Pdfs/Z19M_2.pdf

What's the "orphaned switch"?

Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
longg(at)pjm.com
Guest





PostPosted: Thu Oct 11, 2007 9:53 am    Post subject: [Probable SPAM] Z-19 E Bus feeder questions - Fuse select Reply with quote

Bob,
Re: orphaned switch. Well, not exactly orphaned, it just seems randomly
placed for my situation. Specifically I am applying this to a system
with one ECU and two fuel pumps.

I'm on board with expected loads for the ebus and the system routing
stuff. The primary power and secondary power are set. If we loose
primary power, we turn on secondary - no problem.

If pump #1 is burning (figuratively) up and we turn on #2 (already has a
power source), we still have power to pump #1. Ok, you know these
automotive jobs will die quickly with no fuel pump, so if pump #1 fails
we need to turn on pump #2. Not a problem, but there is some delay
there. A more robust way may might be to use a pressure switch to catch
#1 in the event of a failure and flip over to #2 auto-magically.

Given all that I would like to isolate #1 should the above events occur.
I would like to add auto failover or at least have the ability to switch
each fuel pump on independent of each other regardless of their
relationship to primary or secondary power.

I agree with your thoughts on limiting the e-bus (in an emergency) to
bare bones equipment, however the diagram showing the primary feed as 7
amps would be inadequate for normal use even if I only used the com
(shown 7 amps). Ok, so all of this can vary - no problem.

I would probably have an issue if under emergency mode I forget to shut
down all but non-essential (probably dark, smoke or some other ugliness)
and flip on my little 10 amp eBus alternate only to find I've just blown
a fuse which I can't replace at the moment (busy flying). I believe I
can adjust that logic and the diagram to fit.

Perhaps select items like the MX20 and 530W should be split out onto
another bus to bring the total load down. My setup is a more complex IFR
support. Just more considerations.

There rest of the diagram looks solid (at least from my understanding).
One question? Do I need both the shunt and the ANL in front of the
alternator as shown? My Subaru has the built in regulator, but I would
still like to add an OV protection module.

Thanks

--


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group