At 10:33 AM 6/1/2008 -0700, you wrote:
Quote: |
I'm working on a version of Z-20 for my Jab/X-Air and as I'm an electrical
newbie I wanted to run a couple of things by the group to check that I'm
staying on track:-
On the Power Master Switch am I right in thinking that the 2-10 has it's
first ON for just the battery and the second ON for Battery + Alternator?
|
correct
Quote: | Also, in the Z Figures, where there is no recommended wire size for the
ground wire what should I do? For example from the ALT OV Disconnect
Relay to FWL G2 and also from the Crowbar Over Voltage module to PNL
G3? I'm guessing that for all of the rest I'd just use the same AWG size
as I use from the main bus?
|
All wires in series for any circuit would be
the same size. In the two cases you cited, 22AWG
is sufficient.
All other wires should be sized according to
the current they're intended to carry. Protective
devices (fuses/breakers) are similarly selected.
See wire sizing chart at:
http://aeroelectric.com/articles/Wire_Chart.pdf
Bob . . .
----------------------------------------)