flyadive(at)gmail.com
Guest





PostPosted: Mon Nov 01, 2010 2:28 pm    Post subject: AMP METER & SHUNT Reply with quote

Hi David;

You do not require two shunts.  Only one shunt and a meter capable of reading both Positive and Negative current flow.  


If I may, let me describe what a SHUNT is and why it is required.
A SHUNT is exactly what the word says it is... "A way around", "To circumvent" as in a Shun-pike - A way around a pike.
Why are there shunts?  It is not practicable to manufacture an AMMETER for ever current range required by different applications.  So, there are some basic Ammeters at basic current levels:  100 uA. 1 mA, 100 mA & 1 A.
The SHUNT is placed in PARALLEL with the above ammeter(s) to divert the HIGH current around the Meter, while allowing the small amount through the meter.  
For example:-
If you wanted to read 10 Amps you may use a 1 Amp Meter with a SHUNT capable of carrying 9 Amps.
The meter reads 0 to 1 and that would be 0 to 10 Amps with the shunt installed.


How is the value of the shunt determined?
By RESISTANCE.
If the Meter has an internal resistance of say 100 Ohms the Shunt must carry a ratio of (X):
1 Amp is to 100 Ohms  
as
9 Amps is to X Ohms
---> WHY 9 AMPS?  Because since the Shunt is in Parallel with the 1 Amp meter ...
1 Amp goes through the meter and 9 amps goes through the shunt. A total of a 10 Amp flow.


100 / 9 = 11.11 Ohms for the SHUNT value.


Now I arbitrarily picked 100 Ohms and 1 Amp for the meter.
The real value of the meter would probably be closer to 12 Ohms.


Now, You Can Not just put a DMM across a meter to find the resistance.  Because the DMM would load down the meter and give an incorrect reading.  This would be indicated by a deflection of the ammeter needle.  OF COURSE - If the amperage of the un-shunted meter was high enough there would be less loading of the DMM.
Did this confuse ya?  I could go more in depth if anyone is interested  Sad  


One more NOW - The direction of the current does not mater, NOT to the shunt... Dave, you do NOT need anymore than ONE SHUNT.  The direction ONLY mater to the Meter.


OK, DONE - - - Phew!

--
Barry
[quote][b]


- The Matronics JabiruEngine-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?JabiruEngine-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> JabiruEngine-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group