PostPosted: Thu Jul 12, 2012 7:48 am    Post subject: Battery question not aeroplan related Reply with quote

Hello Bob and all,

as it is not directly aeroplane related I apologize and hope it is still
acceptable to post in that area, at the end it's about batteries an
their differences

I have an UPS which I neglected a bit and it failed recently; the
batteries in there had an ugly shape but no spill, voltage was
below 2V for each (12v 7.2A nominal)

I looked now for replacement from Panasonic (using a 17A and now 20A
since years in my plane). Interestingly enough they have two types
of this:

LC-R127R2PG1
UP-VW1245P1

price difference (in Switzerland) is 28CHF for the 1st and 49.80CHF for
the 2nd, that is quite a bit as I need a set of 4 . We have a bit an
unstable (overloaded) power net so the UPS does get in action at least
once a month.

I had a hard time to identify any facts why I should go the more
expensive way (a general statement, that UP-VW has double the life of a
LC-R was all I found).

Any recommendation you could give in that case?

Many thanks for the great support of this list!

Werner

do not archive


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Jul 12, 2012 9:46 am    Post subject: Battery question not aeroplan related Reply with quote

At 10:48 AM 7/12/2012, you wrote:
Quote:


Hello Bob and all,

as it is not directly aeroplane related I apologize and hope it is
still acceptable to post in that area, at the end it's about
batteries an their differences

I have an UPS which I neglected a bit and it failed recently; the
batteries in there had an ugly shape but no spill, voltage was
below 2V for each (12v 7.2A nominal)

I looked now for replacement from Panasonic (using a 17A and now 20A
since years in my plane). Interestingly enough they have two types
of this:]

Have you considered automotive batteries for this
application? My UPS here has a regular car battery
sitting outside the case connected to nice fat wires
that extend the leads for a battery normally inside
the case.

I can get a lot more capacity for less dollars as
long as it's not a requirement that the battery
'fit inside'.

How old was your original battery? The fact that
it failed and changed shape suggests an overcharge
condition. What ever your choice of battery, you
might want to put a voltmeter on the battery and
watch it for a few weeks and in particular after
a power-outage event to watch the re-charge event.

When all topped off, the battery should be floated
at no more than 13.8 volts and no less than 13.0
volts. In other words, too low to allow the battery
to be charged and too high to allow the battery to
take on 'load'.

My UPS battery is about 50A.H. It will keep my
desk system up for 5 hours or more.
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
glastar(at)gmx.net
Guest





PostPosted: Thu Jul 12, 2012 12:48 pm    Post subject: Battery question not aeroplan related Reply with quote

Thanks Bob, find my answers inside
Quote:

Have you considered automotive batteries for this
application?

The UPS is rack mounted and uses 4 batteries always 2 in series so I
guess I will try tomorrow if I can test with two in series if it works
(I've tried already with one but it did not work (I guess it's using 24 V)
Quote:


Quote:
How old was your original battery? The fact that
it failed and changed shape suggests an overcharge
condition. What ever your choice of battery, you
might want to put a voltmeter on the battery and
watch it for a few weeks and in particular after
a power-outage event to watch the re-charge event.
They were over 10 years old and I've got some warnings, but as these

were LED's only and I had the operation manual not at hand I neglected
for several weeks that then caused probably to overload as some cells
were dead.

Cheers Werner

do not archive


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group