PostPosted: Tue Sep 10, 2013 12:12 am    Post subject: OT: bad circuit breaker? Reply with quote

Final report on the air conditioner problem. As I was standing there watching the unit with the amp meter around the wire to the compressor I saw it jump from about 9 amps (which was too high anyway) and saw it jump to 16+ amps and then the breaker opened. The motor is shot.

Thanks to everyone who consulted on this problem.
Quote:
Raymond Julian
Kettle River, MN.

"And you know that I could have me a million more friends,
and all I'd have to lose is my point of view." - John Prine
On 08/24/2013 10:10 PM, rayj wrote:

[quote] Ken,

I've owned it since new and used it in the same application for years. It takes at least 5 min and maybe more for the current to creep up. It puts out cold air when it's running, so I'm guessing it's the compressor motor. I gave it a good cleaning before I installed it this summer and it operated correctly for more than a month. It's a small window unit so if I can't tinker it back to life it'll be less expensive to replace than to have someone work on it. I'll check everything you mentioned. Thanks very much for the advice.
Quote:
Raymond Julian
Kettle River, MN.

"And you know that I could have me a million more friends,
and all I'd have to lose is my point of view." - John Prine
On 08/24/2013 09:51 PM, Ken wrote:

Quote:
--> AeroElectric-List message posted by: Ken <klehman(at)albedo.net> (klehman(at)albedo.net)

Ray

I look for dirty condenser fins, slow turning fan, or dented restricted high pressure line all of which cause high current.

Then I make sure the compressor really is starting and coming up to speed. ie it is not just a bad starting capacitor or start relay keeping the start winding running and tripping the breaker in a few seconds after startup. There are several clues when that happens but it may not be obvious as the compressor does appear to start up.

If I don't own it I then advise replacing the unit.

If I do own it and it is expensive (or I feel like tinkering), I start wondering about it's history and whether there is any moisture in the refrigerant or someone has put the wrong refrigerant in so I evacuate, dry, and put in new refrigerant. Then I'd follow my advice to others in the above paragraph.

Ken
(no expert but I've done some HVAC work)
do not archive

On 24/08/2013 10:06 PM, rayj wrote:
Quote:
I've got the unit out. I'll check, but I'm willing to bet it's the
compressor. I can't imagine the fan consuming that much energy and not
self destructing. And something resets after a short while and the cycle
starts over.





























[b]


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum


Powered by phpBB © 2001, 2005 phpBB Group