Posted: Sat Jan 07, 2006 2:34 pm Post subject: Z14 Failure Modes and the Cross-Tie |
|
|
I'm laying out the electrical system for my all-glass, all-electric,
FADEC-powered Lancair Legacy. The Z-14 system seems like the natural way to
go, using two full-size alternators. It would be very attractive to have the
ability to power both the A and B buses and recharge both batteries from a
single alternator when needed. However, I'm having trouble imagining a
failure mode where the cross-tie could be used in flight.
If the Bus A alternator's field breaker trips in flight (for example), would
it be safe to engage the cross-tie? You don't know what caused the failure,
and tying the A and B buses together could knock out the B bus.
If you get a low voltage warning on bus A, do you pull the corresponding
field breaker and engage the cross-tie? Again, if something is shorting out
the bus (such as shorted windings on the alternator), you are in danger of
overloading bus B.
Any thoughts?
Adam Molny
Legacy #151
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
 |
klehman(at)albedo.net Guest
|
Posted: Sat Jan 07, 2006 5:58 pm Post subject: Z14 Failure Modes and the Cross-Tie |
|
|
Hi Adam
I figure the most likely reason to close the crossfeed is when one
alternator simply stops producing power or has been shutdown by the OV
protection. Bus voltage will be nominal battery voltage in such a case.
With a contactor on the output of an IR regulator even the stator and
diodes are out of the circuit when I shut down an alternator or the OVP
activates but I'd expect the alternator fuse/breaker/ANL to already be
open anyway in that case. I agree that it might be unwise to close the
crossfeed if immediately after the low voltage warning you observe that
the voltage is below normal battery voltage but then again you have the
option if you need the equipment and think maybe you've got a open
circuited or disconnected battery (or open master contactor) that has
allowed a subsequent OV excursion and alternator shutdown. Plan A would
be to leave it alone til on the ground if I don't need it. Any smoke or
sparks would definately keep my finger away from the crossfeed. There
really isn't much of a "bus" on a small airplane with fuse blocks which
makes it very difficult to imagine a shorted bus. Z-14 also gives the
option of conducting a single alternator recovery flight home or to a
maintanance facility.
Ken
Adam Molny wrote:
I'm laying out the electrical system for my all-glass, all-electric,
FADEC-powered Lancair Legacy. The Z-14 system seems like the natural way to
go, using two full-size alternators. It would be very attractive to have the
ability to power both the A and B buses and recharge both batteries from a
single alternator when needed. However, I'm having trouble imagining a
failure mode where the cross-tie could be used in flight.
If the Bus A alternator's field breaker trips in flight (for example), would
it be safe to engage the cross-tie? You don't know what caused the failure,
and tying the A and B buses together could knock out the B bus.
If you get a low voltage warning on bus A, do you pull the corresponding
field breaker and engage the cross-tie? Again, if something is shorting out
the bus (such as shorted windings on the alternator), you are in danger of
overloading bus B.
Any thoughts?
Adam Molny
Legacy #151
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
 |
klehman(at)albedo.net Guest
|
Posted: Sat Jan 07, 2006 7:43 pm Post subject: Z14 Failure Modes and the Cross-Tie |
|
|
Hi Adam
I figure the most likely reason to close the crossfeed is when one
alternator simply stops producing power or has been shutdown by the OV
protection. Bus voltage will be nominal battery voltage in such a case.
With a contactor on the output of an IR regulator even the stator and
diodes are out of the circuit when I shut down an alternator or the OVP
activates but I'd expect the alternator fuse/breaker/ANL to already be
open anyway in that case. I agree that it might be unwise to close the
crossfeed if immediately after the low voltage warning you observe that
the voltage is below normal battery voltage but then again you have the
option if you need the equipment and think maybe you've got a open
circuited or disconnected battery (or open master contactor) that has
allowed a subsequent OV excursion and alternator shutdown. Plan A would
be to leave it alone til on the ground if I don't need it. Any smoke or
sparks would definately keep my finger away from the crossfeed. There
really isn't much of a "bus" on a small airplane with fuse blocks which
makes it very difficult to imagine a shorted bus. Z-14 also gives the
option of conducting a single alternator recovery flight home or to a
maintanance facility.
Ken
Adam Molny wrote:
I'm laying out the electrical system for my all-glass, all-electric,
FADEC-powered Lancair Legacy. The Z-14 system seems like the natural way to
go, using two full-size alternators. It would be very attractive to have the
ability to power both the A and B buses and recharge both batteries from a
single alternator when needed. However, I'm having trouble imagining a
failure mode where the cross-tie could be used in flight.
If the Bus A alternator's field breaker trips in flight (for example), would
it be safe to engage the cross-tie? You don't know what caused the failure,
and tying the A and B buses together could knock out the B bus.
If you get a low voltage warning on bus A, do you pull the corresponding
field breaker and engage the cross-tie? Again, if something is shorting out
the bus (such as shorted windings on the alternator), you are in danger of
overloading bus B.
Any thoughts?
Adam Molny
Legacy #151
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
Back to top |
|
 |
klehman(at)albedo.net Guest
|
Posted: Sun Jan 08, 2006 1:25 pm Post subject: Z14 Failure Modes and the Cross-Tie |
|
|
Hi Adam
I figure the most likely reason to close the crossfeed is when one
alternator simply stops producing power or has been shutdown by the OV
protection. Bus voltage will be nominal battery voltage in such a case.
With a contactor on the output of an IR regulator even the stator and
diodes are out of the circuit when I shut down an alternator or the OVP
activates but I'd expect the alternator fuse/breaker/ANL to already be
open anyway in that case. I agree that it might be unwise to close the
crossfeed if immediately after the low voltage warning you observe that
the voltage is below normal battery voltage but then again you have the
option if you need the equipment and think maybe you've got a open
circuited or disconnected battery (or open master contactor) that has
allowed a subsequent OV excursion and alternator shutdown. Plan A would
be to leave it alone til on the ground if I don't need it. Any smoke or
sparks would definately keep my finger away from the crossfeed. There
really isn't much of a "bus" on a small airplane with fuse blocks which
makes it very difficult to imagine a shorted bus. Z-14 also gives the
option of conducting a single alternator recovery flight home or to a
maintanance facility.
Ken
Adam Molny wrote:
I'm laying out the electrical system for my all-glass, all-electric,
FADEC-powered Lancair Legacy. The Z-14 system seems like the natural way to
go, using two full-size alternators. It would be very attractive to have the
ability to power both the A and B buses and recharge both batteries from a
single alternator when needed. However, I'm having trouble imagining a
failure mode where the cross-tie could be used in flight.
If the Bus A alternator's field breaker trips in flight (for example), would
it be safe to engage the cross-tie? You don't know what caused the failure,
and tying the A and B buses together could knock out the B bus.
If you get a low voltage warning on bus A, do you pull the corresponding
field breaker and engage the cross-tie? Again, if something is shorting out
the bus (such as shorted windings on the alternator), you are in danger of
overloading bus B.
Any thoughts?
Adam Molny
Legacy #151
|
AdmID:83E83C29680237C6A7B9D0D346BF94A9
AdmID:699E6044ECE49308DB21D9330AB77D81
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|
|
klehman(at)albedo.net Guest
|
Posted: Sun Jan 08, 2006 2:05 pm Post subject: Z14 Failure Modes and the Cross-Tie |
|
|
Hi Adam
I figure the most likely reason to close the crossfeed is when one
alternator simply stops producing power or has been shutdown by the OV
protection. Bus voltage will be nominal battery voltage in such a case.
With a contactor on the output of an IR regulator even the stator and
diodes are out of the circuit when I shut down an alternator or the OVP
activates but I'd expect the alternator fuse/breaker/ANL to already be
open anyway in that case. I agree that it might be unwise to close the
crossfeed if immediately after the low voltage warning you observe that
the voltage is below normal battery voltage but then again you have the
option if you need the equipment and think maybe you've got a open
circuited or disconnected battery (or open master contactor) that has
allowed a subsequent OV excursion and alternator shutdown. Plan A would
be to leave it alone til on the ground if I don't need it. Any smoke or
sparks would definately keep my finger away from the crossfeed. There
really isn't much of a "bus" on a small airplane with fuse blocks which
makes it very difficult to imagine a shorted bus. Z-14 also gives the
option of conducting a single alternator recovery flight home or to a
maintanance facility.
Ken
Adam Molny wrote:
I'm laying out the electrical system for my all-glass, all-electric,
FADEC-powered Lancair Legacy. The Z-14 system seems like the natural way to
go, using two full-size alternators. It would be very attractive to have the
ability to power both the A and B buses and recharge both batteries from a
single alternator when needed. However, I'm having trouble imagining a
failure mode where the cross-tie could be used in flight.
If the Bus A alternator's field breaker trips in flight (for example), would
it be safe to engage the cross-tie? You don't know what caused the failure,
and tying the A and B buses together could knock out the B bus.
If you get a low voltage warning on bus A, do you pull the corresponding
field breaker and engage the cross-tie? Again, if something is shorting out
the bus (such as shorted windings on the alternator), you are in danger of
overloading bus B.
Any thoughts?
Adam Molny
Legacy #151
|
AdmID:83E83C29680237C6A7B9D0D346BF94A9
AdmID:699E6044ECE49308DB21D9330AB77D81
AdmID:F24EE12554874507101161E0190BA573
| - The Matronics AeroElectric-List Email Forum - | | Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
http://www.matronics.com/Navigator?AeroElectric-List |
|
|